Bill,
 
I would just use the eQUEST defaults for whichever ERV-RECOVER-TYPE is
applicable. The variables I would focus on are the sensible, and if
appropriate, latent effectiveness, as well as the ERV-OA-FLOW and
ERV-EXH-FLOW. The effectiveness and/or efficiency are provided by the
HRV/ERV manufacturer. Note that "efficiency" and "effectiveness" mean
different things, and if you enter the efficiency in eQUEST instead of
sensible/latent effectiveness you will underestimate the energy savings.
See HVI (Home Ventilation Institute), Section 3, page two:
http://www.hvi.org/resourcelibrary/proddirectory.html
 
The manufacturer might have values for the air film resistance fraction
and exponent, but don't count on it. These values modify the
effectiveness based on hourly OA and exhaust airflows, so they won't
even matter unless the hourly airflows through the ERV/HRV change
significantly.
 
Regards,
Bill
 
 
 
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of BLafley
Sent: Thursday, June 02, 2011 4:59 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Heat Recovery question
 
Hello,
 
Can someone tell me where I get the following values and/or what are 
reasonable numbers for these inputs?  "HX Air Film Resist."  and "Air 
Film Resist Exp."
 
Thanks,
 
 
-- 
Visit us online! <http://www.cetonline.org>
 
Bill Lafley <mailto:blafley at cetonline.org> | Energy Analyst
Center for EcoTechnology | 320 Riverside Drive - 1A | Florence MA  01062
413-586-7350 ext. 222 | 413-695-2730 (cell)
www.cetonline.org <http://www.cetonline.org> | Sign up for EcoUpdates! 
<http://www.cetonline.org/Mailist/VR_Signup.php>
 
 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110603/7671819e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20862 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110603/7671819e/attachment.jpeg>
    
    
More information about the Equest-users
mailing list