[Equest-users] DHW Savings LEED NC 2.2
    Tai Lieu 
    tailieu at gmail.com
       
    Wed Jun  1 08:20:24 PDT 2011
    
    
  
Hello  All
We're being audited on the energy model for the dhw saving.  I'm just
wondering if this make sense and from your experience if it would be
acceptable to the LEED reviewer.
What I've done is taken numbers from ASHRAE Handbook HVAC Applications DHW
consumption per fixture for office use.
7.6 L / hr for lavatory fixtures
Showers, kitchen sinks, and Lavatory sinks.
Service sinks I'm not quite sure whether i should include all 5 service
sinks (one on each level) or just one sinks since there won't be any mopping
done since most of the building Under floor air distribution and i'll do a
write up of course to explain my reasoning.
I took the consumptions per fixture numbers multiplied by the amount of
fixture then by the demand factor given.
7.6 L/h x 55 # of fixtures x 0.3 demand factor
for each type i took the savings percentage based on each fixture. So
baseline is 2.5 and proposed case is .5 for lavatory fixtures
.5 proposed case  / 2.5 base case
So the proposed domestic hot water demand is 25.08 L / hr or 0.11 gpm.
The reviewer had asked for percentage of hot water vs cold water, and
temperature at the fixtures, i found that harder to substantiate.  So I
thought this process would be a lot better.
Tai Lieu
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110601/b684fc24/attachment.htm>
    
    
More information about the Equest-users
mailing list