[Equest-users] roof modeling
Nick Caton
ncaton at smithboucher.com
Wed Aug 24 13:59:03 PDT 2011
I have a hunch this is explicitly model-able using eQuest… but my experience with DAYSIM is limited and that may be the better approach.
Here’s what I would do:
If those are vertical fenestrations with tilted opaque surfaces (I’m assuming – the image resolution may be misleading me), and assuming the skylights are within one common zone, then my approach would be modeling the top zone as a single “box” within the wizards, then in detailed and within that zone:
- Subtract the summed “cut” area of the skylight wells from the horizontal roof surface area.
- Define (copy) a series of vertical exterior wall surfaces of the appropriate orientation and dimensions to host the vertical skylights. Locate and orient them correctly over the roof to accurately model shading of the horizontal roof surface and of each other.
- Additionally define/copy a series of tilted roof surfaces to model the opaque portions of the skylights. Again locate with some relative accuracy to avoid over/underestimating the effects of their shading upon other elements.
- Define the skylights themselves simply as a series of windows in the new walls.
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Otto Schwieterman
Sent: Wednesday, August 24, 2011 3:35 PM
To: Yuvaraj Saravanan; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] roof modeling
You will have to use a daylighting program such as DAYSIM and bring the results into eQUEST through schedules.
From: Yuvaraj Saravanan [mailto:Yuvaraj.Saravanan at arup.com]
Sent: Wednesday, August 24, 2011 3:27 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] roof modeling
Dear All,
How do I model a skylight like this in eQuest?
Regards,
Yuvaraj
________________________________________________________________________________________
Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
designated individual or entity. If you received this message in error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe unlawful. Any information included in
this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110824/982037f7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110824/982037f7/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 35484 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110824/982037f7/attachment.png>
More information about the Equest-users
mailing list