I hope we're at a simple vocabulary disconnect here...
* Upgrading the windows will reduce your solar cooling loads.
* Reducing your solar cooling loads will reduce the amount of
heat to be removed from the building.
* Reducing the amount of heat to remove will reduce the required
hours of operation of your HVAC system (in this case, evaporative
coolers) to maintain comfort.
* Reducing the runtime of your evaporative coolers will result
in reduced energy consumption. Fan energies primarily, in the case of
evaporative coolers.
* In the event the existing system is not of sufficient capacity
to begin with, you may also/instead observe a reduction in unmet cooling
hours.
The reduction of solar loads with a glazing upgrade could be negligible
for a variety of possible reasons, but it's unlikely the net effect is
absolutely zero.
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: deepika khowal [mailto:deepika.khowal at gmail.com]
Sent: Tuesday, August 16, 2011 3:11 PM
To: Nick Caton
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] evaporative coolers in equest
This is an existing building with evaporative coolers.
the proposed design to upgrade the windows and check the relative
benefits.
I dont see much benefits in energy because evaporative coolers are
sized based on Cfm and not btus, the savings will be in cfms.
correct me if I am wrong.
is there any other way I can show the benefit in the proposed case if
not HVAC benefits?
Thanks
On Tue, Aug 16, 2011 at 1:00 PM, Nick Caton <ncaton at smithboucher.com>
wrote:
Hi Deepika,
I'm not certain any increase/decrease in cooling loads (such as solar
loads affected by changing glazing) should have any effect on the
reported "space cooling energy" when you're using evaporative coolers.
Direct evaporative (swamp) coolers of the simplest sort have only fan
and pump energies to consider - no refrigerant! I would advise looking
up the Detailed Simulation Reports Summary page 158/160 to review end
use categories and what they cover.
I am unfamiliar with Bridgeport's climate, but as a general rule if I
observed a significant amount of glazing in a space served by a direct
evaporative cooler... I'd be extra cautious to ensure the HVAC designer
is carefully considering condensation and potential for other
humidity-driven issues along the way. I'm most used to seeing them
applied to well-ventilated and/or open-air spaces such as garages and
gyms/hangars.
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com <http://www.smithboucher.com>
From: equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] On Behalf Of deepika khowal
Sent: Tuesday, August 16, 2011 1:36 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] evaporative coolers in equest
Hello all
I am modeling a building in Bridgeport, CA which has evaporative
coolers.
I dont see any benefits if I replace existing clear glass with low-e in
cooling energy consumption.
Did anyone model evaporative coolers/swamp coolers before?
I want to know whether there is a way to show cooling benefit with such
HVAC system.
Thanks
Regards
Deepika
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110816/4bba2a17/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110816/4bba2a17/attachment.jpeg>
More information about the Equest-users
mailing list