[Equest-users] Lighting Schedules

Nick Caton ncaton at smithboucher.com
Wed Aug 10 08:12:22 PDT 2011


Hi Brad!

You can't have one without the other.  eQuest uses both the schedules
and a W/SF figure for each space in tandem.  The schedules provide an
hourly fraction of the defined W/SF, not W/SF values directly.  If you
aren't explicitly defining a unique lighting schedule, it only means
eQuest is creating one for you based on your other inputs in the wizards
(weighted space type allocations alongside the W/SF entered or defaulted
for each space type).  You can observe the net result after closing the
wizards by double clicking on the schedule in the component tree.

~Nick

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com 


-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bradley
Donohue
Sent: Wednesday, August 10, 2011 10:00 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Lighting Schedules

Hello,

I am fairly new to equest and have a quick question about lighting
schedules.  If the lighting schedules are left as undefined but there is
a w/ft2 value entered will equest include  the w/ft2 value in any way?

Thanks,

Brad
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG


More information about the Equest-users mailing list