[Equest-users] Condenser loop control?

Carol Gardner cmg750 at gmail.com
Fri Nov 19 08:52:44 PST 2010


The commands you are looking for are for the cooling tower. See below.

Carol


 Volume 2: Dictionary <volume2dictionary.htm> > HVAC
Components<hvaccomponents.htm>>
CIRCULATION-LOOP <circulationloop2.htm> > Loop Temperature
Control<looptemperaturecontrol.htm>
COOL-SETPT-CTRL

Code word specifies the loop temperature control sequence:

FIXED                         specifies that the loop supply temperature is
controlled to a fixed value, specified by the COOL-SEPT-T

OA-RESET                   specifies that the loop supply temperature is
reset on outdoor air according to the COOL-RESET-SCH.

SCHEDULED                specifies that the loop supply temperature is
controlled to a schedule specified by the COOL-SETPT-SCH.

LOAD-RESET               specifies that the loop supply temperature is
resetso that the valve of the worst-case coil is fully open. The
minimum
reset temperature for a cooling-type loop is MIN-RESET-T. LOAD-RESET is
applicable to any loop serving a chilled-water coil (CHW, PIPE2). It is also
applicable to a condenser-water loop; here this control mode will enable the
cooling tower temperature to float with the load and wet-bulb temperature as
described in the cooling tower sections.

                                  Since a WLHP loop also uses a cooling
tower, LOAD-RESET is applicable to the heat-rejection side of a WLHP loop.
It does not apply, however, to the heating setpoint of a WLHP loop.

                                  This mode maximizes the efficiency of the
primary equipment and minimizes the loop's thermal losses (but at the
expense of pumping energy in a variable-flow loop). Refer to
LOOP-FLOW-RESETfor information on how to minimize the pumping
penalties associated with
this control scheme.


On Fri, Nov 19, 2010 at 5:26 AM, Chris Jones <cj at enersave.ca> wrote:

>  I believe that the CONT-SETPT-CTRL = VARIABLE provides similar control?
>
>
> At 08:16 AM 19/11/2010, Brian Fountain wrote:
>
> In DOE-2.1e, you had the option of condenser loop control by wet-bulb
> reset.  I cannot figure out how to do that in DOE-2.2.  Any suggestions or
> was this option lost in the combining of systems & plants.
>
>
>
> _______________________________________________
> Equest-users mailing list
>  http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> Chris Jones
> 14 Oneida Avenue
> Toronto, ON M5J 2E3.
> Tel.  416-203-7465
> Fax. 416-946-1005
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101119/1737e9f2/attachment.htm>


More information about the Equest-users mailing list