[Equest-users] Fan energy typed in as kW/cfm

Ana N. ananeddav at hotmail.com
Tue Nov 16 05:00:16 PST 2010


Right click on Static in WG  (1.17 in your case) and select Restore Default. Design kW/cfm and Delta T will become available for input.
 
Best,
Ana
 


From: TOPP at orbicon.dk
To: equest-users at lists.onebuilding.org
Date: Tue, 16 Nov 2010 10:22:39 +0100
Subject: [Equest-users] Fan energy typed in as kW/cfm








Hi
 
Just a simple question. I want to type in the fan energy as kW/cfm. But it seems I cannot “activate” that input option. How do I switch from the SUPPLY-STATIC and SUPPLY-EFF to the SUPPLY-DELTA-T and SUPPLY-KW/FLOW option?
 

 
Best regards,

Per Topp 
Senior Projektingeniør 
Installation, El & VVS (Ballerup) 

Tel. dir. +45 44 85 87 09 
Mobile: +45 61 55 60 15 
TOPP at orbicon.dk

Orbicon | Leif Hansen A/S 
Lautrupvang 4B, DK-2750 Ballerup 
Tel. +45 44 85 86 87 Fax +45 44 85 86 78 

P Please consider the environment before printing.

It is possible to edit the contents of this e-mail electronically, therefore we cannot guarantee that it has not been changed after distribution. This e-mail may contain confidential information. Please be notified that if you are not the intended recipient, then you are prohibited from distributing, copying or archiving this e-mail. Please delete the e-mail and contact the sender as soon as possible.
_______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG 		 	   		  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101116/598bd0b9/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 143266 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101116/598bd0b9/attachment.png>


More information about the Equest-users mailing list