[Equest-users] Simulation Error with No Error Report

Pasha Korber-Gonzalez pasha.pkconsulting at gmail.com
Thu Nov 4 10:00:25 PDT 2010


Andy,

if you don't see your error in the BDL file, sometimes it is only written to
the output file.   Open your .sim file for this run and then scroll down as
far as you can....your file should show that it terminated at some error.
There should be some clues at that point as to what maybe causing the
program to terminate.

Pasha

On Wed, Nov 3, 2010 at 10:20 AM, David Eldridge <dse at grummanbutkus.com>wrote:

> If the Ancillary AHU is a DOAS system supplying OA to the other fan
> systems, it will have to be listed first in the INP file among the fan
> systems.
>
> You can move it up to first position in the *.inp file directly. (I don't
> know how to do this within eQuest...anyone?)
>
> Helpful tip:  save a backup copy of any input files you intend to modify
> in text editor if you aren't practiced at editing the files that way.
>
> David
>
> David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, HBDP
> Project Manager
>
> Direct: (847) 316-9224 | Fax: (847) 328-4550
> http://www.grummanbutkus.com
>
> Grumman/Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL
> 60201
> Energy Efficiency Consultants and Sustainable Design Engineers
>
>
>
>
> > -----Original Message-----
> > From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-
> > bounces at lists.onebuilding.org] On Behalf Of Andy Harrison
> > Sent: Wednesday, November 03, 2010 11:03 AM
> > To: equest-users at lists.onebuilding.org
> > Subject: [Equest-users] Simulation Error with No Error Report
> >
> > Hi All,
> >
> > I have a strange EQuest error which is leaving me somewhat at a loss.
> >
> > Although there are no errors with the file on startup, when I try to run
> a
> > simulation it tells me that the run was terminated due to an error but
> does
> > not give me any information about what the error was.  When I search the
> > BDL file for "ERROR" there is nothing there.
> >
> > I attach a screenshot and .inp file.
> >
> > Regards,
> >
> > Andrew
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101104/2dcb33c1/attachment.htm>


More information about the Equest-users mailing list