Andrew,

Create a Dummy space, very small 1ft x 1ft x 1ft with no load and then a
Dummy Zone for it and use this for your zone. I would not use Multi Zone but
rather PSZ if you are supply the fresh air at a constant volume or PVAVS if
it is supplied at a variable volume.

Best,

Carol

On Wed, Nov 3, 2010 at 2:48 AM, Andy Harrison <Andy.Harrison at arup.com>wrote:

> Hi All,
>
> I am trying to model a building which has a minimum fresh air AHU serving
> all zones, each of which also has a local cooling unit.  I was trying to
> model this using a single zone AHU for each zone, with outside air to all
> units coming from the multizone unit, which I created later, however I am
> getting an error saying that the multizone AHU needs to be assigned at least
> one zone.  How can I do this, when all of the zones are assigned to a local
> unit?  If I assign a small zone to get rid of the error, will the multizone
> AHU only be sized for the cooling load associated with this zone?  How can I
> confirm that the multizone AHU is sized for the appropriate fresh air load?
>
> Regards,
>
> Andrew
> ____________________________________________________________
> Electronic mail messages entering and leaving Arup  business
> systems are scanned for acceptability of content and viruses
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>



-- 
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101103/f0a385d6/attachment.htm>


More information about the Equest-users mailing list