Thanks all. That's exactly the information I was looking for

 

--

Andrew MacKay 



 

From: Gregg Liddick [mailto:gliddick at theepstengroup.com] 
Sent: 31 March 2010 15:18
To: Kimberly at NorthernArchitects.com; Andrew Mackay;
equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] ASHRAE baseline building rotation

 

That's correct - in 90.1-2004 Table G3.1.5c in the baseline column
states that the SHGC(all) value should be used for all fenestration.  As
someone else mentioned 90.1-2007 has removed the SHGC(north) values.

 

Best Regards,

Gregg Liddick

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Kimberly Killian
Sent: Wednesday, March 31, 2010 9:38 AM
To: Andrew.Mackay at arup.com; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] ASHRAE baseline building rotation

 

I was recently told by USGBC reviewer to use SHGC all value for all
orientations, all rotations (in other words, ignore north values).

 

 

Kimberly Killian
Northern Architects, Inc.
207 King Street Suite 3
Burlington VT 05401
T: 802-658-1953
F: 802-658-2975

________________________________

Original message
From: "Andrew Mackay"  
To: equest-users at lists.onebuilding.org
Received: 3/31/2010 5:32:49 AM
Subject: [Equest-users] ASHRAE baseline building rotation

ASHRAE Appendix G states that the baseline building glazing should
conform with the 90.1 minimum standards. This is differentiated between
north and other orientations.

 

Therefore my baseline building has low-performance glass on north facade
and higher-performance glass on other facades.

 

My question is when rotating the baseline building during performance
rating method, should the glazing be re-assigned? Ie) should each
rotation meet 90.1 standards or only when the building is in its
original orientation.

 

I'm sorry this isn't a strictly an equest question (equestion?) but I'm
sure lots of you have encountered the same problem.

 

Cheers

--

Andrew MacKay 

 

____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100331/73d4605d/attachment.htm>


More information about the Equest-users mailing list