[Equest-users] ASHRAE baseline building rotation

Dahlstrom, Aaron ADahlstrom at in-posse.com
Wed Mar 31 06:30:11 PDT 2010


A heads up Andrew - I think you are using 90.1-2004 yes? - for a new building?

Appendix G - 2004 Table G.2.1.(c) - says to use SHGCall for the baseline glazing - ie no differention for North-facing glass.

ASHRAE 90.1-2007 eliminated this requirement - but it also eliminated a different allowance for North-glass SHGC - all directions of glass must meet the same SHGC requirement.

Aaron Dahlstrom , PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>



From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Howe, Timothy
Sent: Wednesday, March 31, 2010 9:20 AM
To: Andrew Mackay; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] ASHRAE baseline building rotation

Yes you should re-assign.

________________________________
From: equest-users-bounces at lists.onebuilding.org on behalf of Andrew Mackay
Sent: Wed 3/31/2010 3:32 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] ASHRAE baseline building rotation
ASHRAE Appendix G states that the baseline building glazing should conform with the 90.1 minimum standards. This is differentiated between north and other orientations.

Therefore my baseline building has low-performance glass on north facade and higher-performance glass on other facades.

My question is when rotating the baseline building during performance rating method, should the glazing be re-assigned? Ie) should each rotation meet 90.1 standards or only when the building is in its original orientation.

I'm sorry this isn't a strictly an equest question (equestion?) but I'm sure lots of you have encountered the same problem.

Cheers
--
Andrew MacKay


____________________________________________________________

Electronic mail messages entering and leaving Arup  business

systems are scanned for acceptability of content and viruses


This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100331/a8a106e4/attachment.htm>


More information about the Equest-users mailing list