[Equest-users] loop operation controls
Bishop, Bill
wbishop at pathfinder-ea.com
Fri Mar 19 05:23:49 PDT 2010
Andrew,
I believe the conservative approach, and the intent in Appendix G., is
to keep everything the same between the baseline and proposed models
unless it is specifically addressed by 90.1. I model loop operation the
same in my proposed and baseline designs. "Standby" will use
considerably more pumping energy than the other options so try to
determine how the proposed design will be operated. Dedicated heating or
cooling loops are often operated on seasonal schedules.
Regards,
Bill
William Bishop, EIT, BEMP, LEED(r) AP | Pathfinder Engineers &
Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Andrew
Sent: Friday, March 19, 2010 6:31 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] loop operation controls
Hi!
I'm creating a baseline building with ASHRAE 90.1 and I would like to
know how should I input loop operation controls: Standby or demand.
Thanks to all!!!
Andrew