[Equest-users] Building Square Footage
Rob Hudson
rdh4176 at gmail.com
Tue Mar 16 04:58:21 PDT 2010
That is the same logic i went through, and double checking my plenum zones
have shown that they in fact are all unconditioned or plenum. I can send
out the .inp file or the output reports if people have time to check it
out.
On Tue, Mar 16, 2010 at 3:49 AM, Gaurav Mehta <gmehta75 at gmail.com> wrote:
> Rob/ Pasha,
>
> The kBtu/SF on the BEPS Report and $/SF on ES-D report use the conditioned
> floor area. Please see the LS-C report that shows the conditioned floor area
> you are modeling.
>
> LV-B report does show all the spaces including unconditioned spaces
> and plenums, but the total area is not used in the summary report.
>
> Without looking at your model, I can only make a guess that you might be
> modeling the Plenum zones as 'Conditioned'. By the numbers that you have
> provided:
>
> 9,500 SF x( 3 [floors] + 3 [plenums] ) = 57,000 SF subtract any
> unconditioned spaces and the answer would be ~ 50,000 SF
>
> Please check your inputs for plenum zones under both 'Spaces' and 'Zones'
> and in both, the 'Zone Type' input should either be 'Unconditioned' or
> 'Plenum'.
>
> Hope it helps.
>
>
> Best regards,
>
> Gaurav Mehta
> Sustainable Building Analyst
> Stantec
>
> *From:* Pasha Korber-Gonzalez <pasha.pkconsulting at gmail.com>
> *Sent:* Monday, March 15, 2010 13:40
> *To:* Rob Hudson <rdh4176 at gmail.com>
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Building Square Footage
>
> Hi Rob,
>
> this is a good question and important to understand about how inputs are
> translated to DOE & reported in the output.
>
> Yes you are right that the summary is accounting for the floor area of the
> unconditioned spaces as well and the plenum spaces. If you look at report
> LV-B, summary of spaces in your project you will find the info you are
> looking for.
>
> This report is a listing of all the spaces (or thermal zones) in the
> project. Theis listing incudes both conditioned spaces as well as
> unconditioned spaces and plenums. In reviewing this report, pay special
> attention to the column labeled "space floor multiplier". The total area
> and volume for each space is this value times the area and volume listed in
> the last two columns. The building totals row includes the effect of these
> multipliers, but the area includes plenums and unconditioned spaces as
> well.
>
> Pasha
>
> On Mon, Mar 15, 2010 at 2:02 PM, Rob Hudson <rdh4176 at gmail.com> wrote:
>
>> This seems like a silly question, but i would like some input regardless.
>> My building has three floors, each about 9,500 square feet. However, the
>> looking at the BEPU and other reports are showing a total utility cost of
>> 110632$ and a $/sqft of 2.25. this shows a sqft of about 50,000 for the
>> building. Is this something that i should disregard or is it relevant? I
>> have also modeled the unconditioned space above each room as a separate
>> space. Could the program be combining this plenum space into the sqft of
>> the entire building? Is this plenum sqft affecting the output of the
>> reports? any help is greatly appreciated.
>>
>> --
>> Rob Hudson
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
> ------------------------------
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100316/3da53ea5/attachment.htm>
More information about the Equest-users
mailing list