[Equest-users] Modeling Overhead Radiant Heating

Bishop, Bill wbishop at pathfinder-ea.com
Thu Mar 11 05:55:20 PST 2010


Dennis,
 
You can also try modeling gas fired radiant heaters as baseboards with
BASEBOARD-SOURCE "furnace". The gas use will be calculated using the
FURNACE-HIR at the system level (at least it looks that way from a
parametric run that I did). This becomes a problem if you are also
modeling furnace heating for the system HEAT-SOURCE and it has a
different efficiency, since you can only enter one furnace HIR per
system.
 
Regards,
Bill
 
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.         
________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John
Aulbach
Sent: Thursday, March 11, 2010 1:45 AM
To: Dennis Hunt; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Modeling Overhead Radiant Heating
 
Dennis:
 
Closest thing I can think of is Floor Panel Heating..
 
John Aulbach
 
________________________________

From: Dennis Hunt <dhunt at summitbe.com>
To: equest-users at lists.onebuilding.org
Sent: Wed, March 10, 2010 8:47:23 PM
Subject: [Equest-users] Modeling Overhead Radiant Heating
eQUEST users,
 
Is it possible to simulate a natural gas fired overhead radiant heating
system, similar to that found in an industrial building. If so, what was
the input parameters used?
 
Thanks,
 
Dennis Hunt
503-246-5241
dhunt at summitbe.com
http://www.summitbe.com
Summit Building Engineering
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100311/1e9fad2a/attachment.htm>


More information about the Equest-users mailing list