Michael Daley
MichaelD at Hargis.biz
Wed Mar 10 07:58:48 PST 2010
Tom,
You've stumbled onto one of the items that needs to be updated in the next version of E-Quest. The F-factor is not the same as the U-factor you've indicated on the attached document. The way to correctly account for the heat loss through the slab perimeter is to correlate the F factor to an equivalent U value for input into the program. Take a look at the 2009 ASHRAE fundamentals Chapter 18.30-32 equations 35, 41, and 42 for how to do this. Inputting the F-factor directly for the U value could greatly skew the heat loss that occurs through the slab.
Sincerely,
Michael Daley, PE
Mechanical
HARGIS ENGINEERS
600 Stewart Street
Suite 1000
Seattle, WA 98101
www.hargis.biz<http://www.hargis.biz>
d | 206.436.0469 c | 206.914.5587
o | 206.448.3376 f | 206.448.4450
From: Eckwahl, Tom [mailto:TEckwahl at karpinskieng.com]
Sent: Friday, February 26, 2010 10:29 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] F-Factor
What is the consensus on where F Factor should be input? I have been putting it under the underfloor material data (see attached).
Is this correct?