[Equest-users] Interior LPD Baseline & Proposed
David S Eldridge
DSE at grummanbutkus.com
Mon Mar 8 17:41:45 PST 2010
Appendix G in 2004 says to use the same method of categorization that you use in the proposed building. This would be especially important if the areas of the project have varying schedules or methods of lighting control.
David
http://www.grummanbutkus.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Monday, March 08, 2010 7:36 PM
To: Soham Babu; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Interior LPD Baseline & Proposed
Hi Soham,
I am no USGBC reviewer, but I have submitted comparative models in the past using the "actual" design, and working out an equivalent LPD for the whole building applied uniformly to the spaces. I do not think there is anything preventing you from entering the individual space LPD's in the proposed model, excepting that could take a bit more time. You may find it pushes your energy savings further however depending on the rest of your model.
[cid:image001.jpg at 01CABEF6.66D0E980]
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Soham Babu
Sent: Wednesday, March 03, 2010 12:29 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Interior LPD Baseline & Proposed
Hi all,
In the baseline interior LPD I have gone with building area method, but for proposed the electrical floor plans as given space by space LPD ,if I go with space by method in proposed ASHRAE recommends ? or shall I have to go with both identical like if I follow building area method in baseline identical in proposed if yes, than can I take average LPD of the all spaces?
Any help will be greatly appreciated
Kind Regards
Soham babu
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100308/4abeb436/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100308/4abeb436/attachment.jpg>
More information about the Equest-users
mailing list