[Equest-users] Pump Gas Consumption?
Gaurav Mehta
gmehta75 at gmail.com
Mon Mar 8 07:06:07 PST 2010
Omer,
Its not gas consumption for pumps, but represents energy consumed by the pilot light for the furnace. The new technology has in fact done away with pilot lights, therefore, newer equipments do not consume this energy, and can be set to 0.
When you create a system with gas furnace heat, by default the Furnace Fuel Auxiliary is set at 800 Btu/h.
Change it to 0 and gas consumption under Pump & Aux will disappear.
Please see the excerpt from DOE-2 help and the screen-shot below:
FURNACE-AUX
The rate of energy use of the furnace pilot. For a gas-fired furnace, this is the energy consumed by the pilot light when there is no load on the furnace. In this case the program assumes that the pilot light consumption when the furnace is "on" is included in FURNACE-HIR-FPLR. For an oil-fired furnace, FURNACE-AUX is the energy consumed by the spark ignition and the fuel pumping system when there is a load on the furnace. In this case, the auxiliary energy consumed in a given hour is FURNACE-AUX times the part load ratio that hour (therefore, no energy is consumed when there is no load on the furnace). This auxiliary fuel is allocated to the AUX-FUEL-METER.
Best regards,
Gaurav Mehta
Sustainable Building Analyst
Stantec Consulting Services Inc.
From: Ömer Moltay
Sent: Monday, March 08, 2010 02:51
To: eQUEST Users List
Subject: [Equest-users] Pump Gas Consumption?
Dear All,
For my baseline model, involving System 5 Packaged VAV as well as a few System 3's, I am having small but steady gas consumption under the heading "Pumps & Aux". The consumption is about 1,000,000 BTU each month. In total, I have 13,700,000 BTU of pump gas consumption compared to 2,444,700,000 BTU of space heating gas consumption.
Why gas consumption for pumps? Some new technology I do not know about? Or is this something for auxiliary under "Pumps & Aux", which again I have no idea what it could be.
Thanks for any replies,
Ömer Moltay, LEED AP
Mimta Ltd.
Hekimsuyu Cad. 559. Sk. No:39
34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
www.mimtarch.com
--------------------------------------------------------------------------------
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100308/0f5c1321/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/bmp
Size: 1155714 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100308/0f5c1321/attachment.bin>
More information about the Equest-users
mailing list