Adam:
How do you vary flow for a VFD is you aren't varying flow?
And how do you get the air to 110°F if you are leaving the "hot deck" at 80°F?
What did you change in the proposed model over the base model?
An .INP and .PD2 file of each would be helpful.
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
PartnerEnergy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com
________________________________
From: Adam Gonthier <agonthier at Horizon-Engineering.com>
To: equest-users at lists.onebuilding.org; bldg-sim at lists.onebuilding.org; Vidya
Gowda <vgowda at Horizon-Engineering.com>
Sent: Thu, July 29, 2010 1:21:44 PM
Subject: [Equest-users] PSZ Very High Unmet Hours
Dear eQuest users,
I am having some difficulty with a project I am working on, and I was hoping I
could receive some help or any information on a building a with packaged single
zone units with DX cooling and hot water coils for heating, with a VFD to vary
the supply flow (there are no VAV boxes in the system, and the supply reacts to
overall building pressure rather than specific zonal needs determined by
pressure sensors in the ductwork). There is no reheat in the system either.
It is a LEED for schools project where the simulation of the proposed model
shows very high unmet loads for heating and the total energy consumption for
space heating is 199 MBTU which is unrealistically low as compared to the
baseline model space heating which is 6369 MBTU. We do not see many unmet hours
in the control zone, but since the unit supplies many zones, we are getting very
high unmet heating hours in non-control zone spaces. We are seeing on the order
of 4000-5000 hours unmet in many zones.
I have modeled the heating for all zones by specifying the
Heat Source as hot water loop,
The Zone Heat Source is not installed, as the design has no reheat.
Zone entering maximum supply temperature is at 110 degrees.
Hot deck max leaving temp is 80 degrees
Reheat delta T: n/a
Many thanks in advance,
Adam A. Gonthier
Energy Engineer
Horizon Engineering Associates, LLP
347.297.9005
www.horizon-engineering.com
Demand a Higher Standard