[Equest-users] Anomaly Multi zone system

Karen Walkerman kwalkerman at gmail.com
Thu Jul 29 05:17:18 PDT 2010


If you look at the SS-L report, you'll notice that the fan is actually
operating at full volume ~ 94% of the time, and between 90 and 100% capacity
for the other hours.  Then, if you look at the SS-R report, you'll notice
that the number of hours where heating is at 0 -10% flow is roughly
equivalent to the number of hours where the cooling flow is at 90 - 100%.
 You really need to look at this on an hourly basis, instead of in the
summary reports, but things seem to be operating properly when I run the
file.

I did, however, run the file with a Houston, TX weather file as I don't have
the New Delhi weather file.

--
Karen

On Thu, Jul 29, 2010 at 6:35 AM, Siddharth V <siddharth.v at tcs.com> wrote:

>
> Hi Guys,
>
> I was trying to simulate the HVAC performance using a multi zone system. I
> have manually given that the design CFM should be 62485 cfm.
>
> Using the options, I have also included the "Supply Air Flow Rate"  and the
> Power consumed by FAN at the output.
>
> But it seems that the Air flow rate is way below the value given input
> value.
>
> Note that this system is not a VAV system. A constant Air Volume flow was
> also ensured.
>
> I am unable to understand why the system behaves in this way, as when the
> same was done for Dual Duct system, the given CFM was maintained at the
> output.
>
> Please find the attached .zip file containing the project file and the
> excel file containing the flow parameters and the power consumption for the
> 1st 3 months.
>
>
>
>
>
>
> Regards,
> Siddharth Venkataraman
> Tata Consultancy Services
> Mailto: siddharth.v at tcs.com
> Website: http://www.tcs.com
> ____________________________________________
> Experience certainty.        IT Services
>                        Business Solutions
>                        Outsourcing
> ____________________________________________
>
> =====-----=====-----=====
> Notice: The information contained in this e-mail
> message and/or attachments to it may contain
> confidential or privileged information. If you are
> not the intended recipient, any dissemination, use,
> review, distribution, printing or copying of the
> information contained in this e-mail message
> and/or attachments to it are strictly prohibited. If
> you have received this communication in error,
> please notify us by reply e-mail or telephone and
> immediately and permanently delete the message
> and any attachments. Thank you
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100729/847d332a/attachment.htm>


More information about the Equest-users mailing list