[Equest-users] Shell Multipliers

John Aulbach jra_sac at yahoo.com
Sat Jul 17 07:59:48 PDT 2010


Akshay:

As an example, you say you have identical floors. Assuming you are in the SD 
Wizard, you state on Screen One (General Shell Information) that you are using 
floors multipliers (check box) and state the correct number onf florrs. If you 
DO have several shells (for different zoning purposes) make SURE each shell 
multiplies only those identical floors. If you have, say, 3 different shells. 
Shell No 1 x identical floors + Shell 2 x identical floors  Shell 3 x identical 
s floors MUST = 18.

Hope this helps.

John Aulbach




________________________________
From: Akshay Pahade <kce4 at kamalcogentenergy.com>
To: equest-users at lists.onebuilding.org
Sent: Sat, July 17, 2010 5:59:19 AM
Subject: [Equest-users] Shell Multipliers

Hi all,

I am trying to use the shell multipliers to build a residential building with 
identical 18 floors. The model is working fine but there is an issue in the 
areas calculated by the model. It seems that the areas are getting multiplied 
several times. This is thus also affecting the end energy usage results. Can 
anyone please suggest me how to use the shell multipliers just to get the right 
results.



Regards,
Akshay Pahade
Project Engineer,
Kamal Cogent Energy Pvt. Ltd.
Jaipur 

www.kamalcogentenergy.com
kce4 at kamalcogentenergy.com


      