Hi Amber!
I don't enter scheduled capacities or modified scheduled capacities.
G3.1.2.2 says we need to oversize coil capacities by 1.15/1.25 "based on
sizing runs for each orientation." Keeping in mind this is for the
baseline only, basically that section is getting at the requirement to
let the model auto-size these baseline systems based on the same loads
that the proposed systems are sized under (people, ventilation air,
envelope and process loads, etc).
Basically, I don't specify a capacity (allowing eQuest to autosize), and
enter those factors as the cooling and heating sizing ratios under the
appropriate tabs in the airside systems tabs/spreadsheets. This will
up-size the calculated capacities in the manner emulating how an HVAC
designer might for safety (keeping in mind this is often all based on
TMY averaged weather data, which doesn't account for atypical seasons
climactically).
Hope this helps!
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Amber
Welsh
Sent: Friday, July 16, 2010 2:08 PM
To: EQUEST
Subject: [Equest-users] System Compliance Heating and Cooling Values
When asked to input compliance heating and cooling capacities, do you
input scheduled values or multiply scheduled values by 1.15 and 1.25 for
cooling and heating, respectively? Thanks.
Amber Welsh, P.E. | Associate
LEED(r) Accredited Professional
397 5th Street NE,
Atlanta, GA 30308
(v) 404.810.9020
(c) 678.488.1967
timmonsdesigneng.com <http://timmonsdesigneng.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100716/82ba1188/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100716/82ba1188/attachment.jpeg>
More information about the Equest-users
mailing list