[Equest-users] LEED Baseline system
Demba Ndiaye
Demba.Ndiaye at setty.com
Tue Jul 13 12:34:48 PDT 2010
Read “floor” as “story” and you can see the definition of that term in the Standard (Section 3). Basement is specifically excluded. So in the present case, you fall in System 3 or 4.
_____________
Demba NDIAYE
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Dakota Kelley
Sent: Tuesday, July 13, 2010 2:11 PM
To: Ana N.; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] LEED Baseline system
If it is conditioned space (heated, cooled, or both), a basement floor is still a floor as far as system selection is concerned. If it is neither heated nor cooled, it might be acceptable to exclude it, but I admit I have never encountered an entirely unconditioned basement on a LEED project before.
[cid:image003.jpg at 01CB22A0.ED826A90]
DAKOTA KELLEY
Project Designer | Energy Analyst
Office: 214.744.6199
Cell: 214.280.3825
Fax: 214.744.0770
http://www.teliospc.com <http://www.teliospc.com/> 3535 Travis St. Suite 115
dakotak at teliospc.com<mailto:dakotak at teliospc.com> Dallas, TX 75204
| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed,
And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you
are not the intended recipient, please email the sender immediately, and delete this email from all computers. Any
distribution or other use is strictly prohibited. Copyright © 2009 Telios Corporation.
From: Ana N. [mailto:ananeddav at hotmail.com]
Sent: Monday, July 12, 2010 5:39 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED Baseline system
Hi All,
My understanding is that the basement should not be counted toward the total number of floors when selecting the baseline HVAC system type (Table G3.1.1A). My building has three stories plus basement and total conditioned floor area of 20,600 sf ( sf does not include attic which is about 5,000sf). I would select PSZ-AC for hybrid or PSZ-HP for electric heat. Am I correct?
Any comments are appreciated.
Thank you.
Ana
________________________________
Hotmail has tools for the New Busy. Search, chat and e-mail from your inbox. Learn more.<http://www.windowslive.com/campaign/thenewbusy?ocid=PID28326::T:WLMTAGL:ON:WL:en-US:WM_HMP:042010_1>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100713/d554cfdc/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 3170 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100713/d554cfdc/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 2143 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100713/d554cfdc/attachment.jpg>
More information about the Equest-users
mailing list