[Equest-users] Lighting Control - Occupancy Sensor

Patrick J. O'Leary, Jr. poleary1969 at gmail.com
Sat Jul 10 20:45:01 PDT 2010


fyi - even though i wasn't trying to model or claim savings from 
occupancy sensors, i received the following comment on a recent leed review:

"Per ASHRAE 90.1-2004 Section 9.4.1.2, a lighting control device is 
required in classrooms, conference rooms, and lunch and break rooms.

Credit for occupancy sensors cannot be taken in spaces where occupant 
sensors are required by Section 9.4.1.2."

so be sure to check the occupancies before claiming credit for occupancy 
sensors.

On 7/10/10 6:21 PM, Derek Huang wrote:
>
> Does anyone know if there is a spot for Occupancy Sensor lighting 
> controls ? In both of DD Wizard mode and Detailed Data Edit mode, I 
> didn't see any.
>
> Thanks,
>
> **Derek Huang, LEED AP, CPD **
>
> **Mechanical Engineer******
>
> 97 E. Brokaw Road, No 300
>
> San Jose, CA 95112
>
> *Direct*: 408 487-1305
>
> *Fax:*      408 436-1511
>
> www.atce.com <http://www.atce.com/>
>
> derek.huang at atce.com
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>    

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100710/2f837df2/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2266 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100710/2f837df2/attachment.jpeg>


More information about the Equest-users mailing list