[Equest-users] Baseline Rotations as per ASHRAE 90.1
Nick Caton
ncaton at smithboucher.com
Fri Jul 2 07:52:42 PDT 2010
Small rotational differences are typical of buildings with similar
surface areas on the east, west, north, and south elevations. I would
only expect a significant difference if you have a very "long"
footprint, or one side of your building is largely unconditioned along
the perimeter. Conceptually, I suppose we're being "rewarded" for
choosing an optimal orientation rotation on the building site - but if
anything we're really being rewarded for designing "long" building
footprints as they can have a larger difference against the averaged
baseline...
That said, if an architect asks me at a conceptual design stage, the
most thermally efficient building shape considering exterior surface
area is theoretically a hemisphere - barring that a "cubic," compact 3D
shape is better than any "long" shape with larger surface area for the
given volume/footprint. If the goal is to maximize LEED points
(relative baseline performance), you might suggest a thermally
inefficient, but optimally-oriented "long" shape that will do better
than it's averaged baseline... (I wouldn't!) If the goal is to reduce
energy consumption/utilities however for the end-users, reduce the
building shape surface area.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Soham
Babu
Sent: Friday, July 02, 2010 2:29 AM
To: Omar Katanani; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline Rotations as per ASHRAE 90.1
Omar,
Simulation for 4 rotations value will be small difference only, in some
of the cases it will be same also. it all depends upon the building
location & orientation.
Regards
Soham
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar
Katanani
Sent: Friday, July 02, 2010 12:48 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Rotations as per ASHRAE 90.1
Dear all,
I performed a simulation of my baseline building over the 4 rotations.
The difference between the lowest consumption and the highest one out of
the 4 runs was only 1.33% (1,312,500 to 1,329,200 kWh).
Is this a normal value? This is my first project but I thought I would
have a bigger number.
Any advice out of your experience is greatly appreciated.
Many thanks,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel: +961 (0) 1 971 255
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 207 939 0989
Fax: +44 (0) 207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100702/9473d3aa/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100702/9473d3aa/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100702/9473d3aa/attachment-0001.jpeg>
More information about the Equest-users
mailing list