Molly Curtz molly.curtz at arup.com
Mon Jan 25 13:20:42 PST 2010


Hi James, 

Try  TYPE = FRAC/DESIGN

That should work with the -999 values.

 

Best,

 

Molly Curtz, P.E.

Mechanical Engineer

 

Arup

403 Columbia St., Suite 220

Seattle, WA 98104

direct: 206 493 2234

tel: 206 749 9674 ext. 25534

fax: 206 749 0665

molly.curtz at arup.com

www.arup.com

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of James
Hansen
Sent: Monday, January 25, 2010 1:03 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Setting after-hours OA volume to zero
usingMIN-AIR-SCH

 

I want to setup a system where the OA volume is set to 0 for setback
heating/cooling.  Under the help for "Minimum Air Schedule", it says
that you can set up a schedule where the values for min OA range from 0
to 1.0, but a value of -999 defaults that particular hour to whatever
the zone calcs require.

 

This is perfect, except the only type of schedule that you can input
into MIN-AIR-SCH is type FRACTION, and the FRACTION schedule won't
accept -999.  Only from 0 to 1.0.

 

What am I doing wrong?  Thanks in advance,

 

GHT Limited
James Hansen, PE, LEED AP

Senior Associate

1010 N. Glebe Rd, Suite 200

Arlington, VA  22201-4749

703-338-5754 (Cell)

703-243-1200 (Office)

703-276-1376 (Fax)

www.ghtltd.com <http://www.ghtltd.com/> 

 

 

________________________________

The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee.  It is
the property of GHT Limited.  Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful.  If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments.  Thank you.

____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100125/bf2ce65b/attachment.htm>


More information about the Equest-users mailing list