[Equest-users] Weather

Jonathan Curtin jcurtin at WylieAssociates.com
Tue Jan 19 10:06:46 PST 2010


Katie,
 
To the best of my knowledge, when you change the starting date/year in
eQUEST, the only thing you are changing is the day of the week that
applies to the first day of the TMY data. For example, 2010 begins on a
Fri, which sets the number of weekdays and weekends you have in each
month/year (i.e. you'll have 10 combined weekend days in Jan, rather
than only 8 if this month would have started on a Mon (year 20XX). If
your building is unoccupied on the weekend, you'll clearly use less
energy in Jan 2010 than you would in year 20XX.
 
The weather conditions used to simulate that first day in both cases
will always be the same (set by the TMY data file) regardless of the
start year that is specified . If you are comparing simulation runs for
two different years I've found that this generally will have a greater
impact on monthly consumption differences, but overall annual
consumption should still be in the ballpark.
 
If you want to test this, you can set 24/7/365 schedules that do not
change between weekday/weekend/holidays and I bet there will be no
impact of the start year on consumption (with the exception of how
eQUEST handles of Leap Years).
 
I hope this helps.
 
Regards,
 

  Jonathan M. Curtin, EIT, LEED(r) AP
  Mechanical Engineer

 

 


________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Katie
Tuttle
Sent: Tuesday, January 19, 2010 11:05 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Weather



Does anyone know where the weather data for eQuest comes from?  Why I
ask is because many energy modeling applications have requirements on
the type of weather data used for simulation.  What I've noticed is that
if you change the "Run Period" in eQuest (see screen shot below as found
on the "Project & Site" tab in detailed edit mode under "Simulation
Options: Entire Year"), the energy use also changes.  I also found that
if you set the run period to span over multiple years, the output (even
with units per year) adds all of the years together.  Is eQuest not
using a TMY, TMY2 or TMY3 file to create its .BIN files?  If so, why
would the year even matter since you usually want to be using typical
weather data?  Do those years actually correspond to actual data?

 

  

 

My second question (relating to this) is how to use DOEWth to convert
TMY2 files to .BIN files?  Is this the only way to do this?  

 

Thanks,

 

KATIE L. M. TUTTLE EI, LEED(r) AP
Mechanical Designer

 

Henderson Engineers, Inc.   8325 Lenexa Drive  Lenexa, KS 66214
dir 913 742 5508  tel 913 742 5000  fax 913 742 5001   www.hei-eng.com
<http://www.hei-eng.com/> 

 

 


________________________________

This email and any files transmitted with it are confidential and are
intended solely for the use of the individual or entity to whom they are
addressed. This communication represents the originator's personal views
and opinions, which do not necessarily reflect those of Henderson
Engineers, Inc. If you are not the original recipient or the person
responsible for delivering the email to the intended recipient, be
advised that you have received this email in error, and that any use,
dissemination, forwarding, printing, or copying of this email is
strictly prohibited. If you received this email in error, please
immediately notify administrator at hei-eng.com.


------------------------------------------------------------------------------
Legal Disclaimer: The information contained in this communication is confidential and is covered by the Electronic Communications Privacy Act, 18 U.S.C. §§ 2510-2521; it may be privileged and is intended for the exclusive use of the above named addressee(s). If you are not the intended recipient(s), you are expressly prohibited from copying, distributing, disseminating, or in any other way using any of the information contained within this communication. If you have received this communication in error, please contact the sender by telephone at (713) 781-2526 or by response via email and permanently delete the original email (including attachments) and any copies.

Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100119/17a8bf7a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 14575 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100119/17a8bf7a/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 5566 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100119/17a8bf7a/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5651 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100119/17a8bf7a/attachment.jpeg>


More information about the Equest-users mailing list