[Equest-users] Baseline Pump Power
Kevin Kelly
kkelly at r3energy.com
Thu Jan 14 13:51:17 PST 2010
James is right.
The way that we were taught to do it was:
"There are several approaches to model 19W/GPM pump power. In one approach,
a simulation can be
performed without entering inputs for pump flow and pump power. The eQuest
report "PV-A Plant
Design Parameters" provides software generated values for pump power and
pump flow. This report
should always be used to verify the W/GPM of the baseline pumps. If the
ratio of pump power to pump
flow is equal to 0.019 kW/GPM, the pump power is ASHRAE compliant. If not,
the mechanical
efficiency should be modified to increase or decrease pump power.
Alternatively, the pump power input
can be modified. However, the flow rate should not be modified in the
baseline model since this may
result in unintended eQuest errors. Please note that as screenshot below
shows, 19 W/GPM
consumption is about equal to a pump having 60% combined motor and
mechanical efficiency operating
at 60ft head. Please refer to note 6 of ASHRAE 90.1 -2004 Table 11.3.2 A for
additional clarification."
Cheers,
Kevin Kelly, LEED AP
Energy Systems Analyst
R3 Energy Management
W: 914.909.3940 x115
kkelly at r3energy.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of James
Hansen
Sent: Thursday, January 14, 2010 4:09 PM
To: Eckwahl, Tom; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline Pump Power
First you have to pull out the loop/pump flow from the PV-A report, then
multiply by 19 W, and enter that as the pump KW. I think you also have to
set the pump/motor efficiencies to 1.0 since the ASHRAE 90.1 value of 19 W /
gpm should automatically include losses. Someone feel free to correct me on
that if it's not right.
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
<http://www.ghtltd.com/> www.ghtltd.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eckwahl,
Tom
Sent: Thursday, January 14, 2010 3:59 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Pump Power
This question has been asked before but I could not find that a response was
posted to the forum. Baseline case hot water pump power is 19 W/gpm, where
is this value input?
Thomas N. Eckwahl
Project Engineer, Mechanical
karpinski
ENGINEERING
_____
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is the
property of GHT Limited. Unauthorized use, disclosure or copying of this
communication or any part thereof is strictly prohibited and may be
unlawful. If you have received this communication in error, please notify
me immediately by return e-mail or by e-mail to <mailto:ght at ghtltd.com>
ght at ghtltd.com, and destroy this communication and all copies thereof,
including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100114/5b66d894/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 29920 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100114/5b66d894/attachment.png>
More information about the Equest-users
mailing list