Lori,
 
I would model the third floor mansard roof as a vertical exterior wall
with a different construction (and new construction layers). Enter the
appropriate setback distance for the windows in the mansard roof. You
can model the 4' mansard roof extension and porch roof with building
shades. (In DD Edit mode, within the Building Shell module, right-click
on the Project in the Component Tree and select Create Building Shade.)
 
Regards,
Bill
 
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.             
________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Lori
Dowles
Sent: Tuesday, January 12, 2010 2:36 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Mansard Roofs & Porch Overhangs
 
Hi All,
The 3-story building I am modeling has a flat roof with a decorative
mansard roof extending above the flat roof by about 4' and going down to
the bottom of the top floor. In addition, there is a porch wrapping
around the East & South side of the building with an overhang which is
attached to the building.
 
Can anyone shed some light on how I can incorporate these elements into
my model? An overhang won't work because they are not based off windows,
and in the case of the mansard, roof surround the top floor windows.
 
I've attached 2 dwgs showing these conditions. Help?!
 
Thanks,
Lori
 
 
        Lori Dowles, LEED Green Associate
        The Martin Group LLC
        138 Jackson Street
        Matawan, NJ 07747
        ph. 732.441.0006
        fx.  732.441.7020
        ldowles at martingroupservices.com
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100112/1b25d972/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 40892 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100112/1b25d972/attachment.jpeg>


More information about the Equest-users mailing list