[Equest-users] equest crashing on chilled water loop primaryselection
RobertGChronic at Eaton.com
RobertGChronic at Eaton.com
Mon Dec 20 09:32:09 PST 2010
Since this is a campus connection, I only wanted the load of the chilled
water and not necessarily size a chiller plant. I thought the easiest
way was to "replace" the plant with a meter and have the meter tally up
the loads. I certainly would welcome any feedback if there are better /
easier ways to model a campus chilled water connection.
Thanks!
From: Shaun Martin [mailto:smartin at shaunmartinconsulting.com]
Sent: Wednesday, December 15, 2010 6:12 PM
To: Chronic, Robert G; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] equest crashing on chilled water loop
primaryselection
You only seem to have a chilled water meter attached to this loop - no
primary equipment (chiller) so there is nothing to size to.
Shaun Martin LEED AP
Principal
Shaun Martin Consulting
Suite 200 - 420 West Hastings Street
Vancouver BC V6B 1L1
604-789-1095
smartin at shaunmartinconsulting.com
<mailto:smartin at shaunmartinconsulting.com>
member CAGBC, ASHRAE
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
RobertGChronic at Eaton.com
Sent: Wednesday, December 15, 2010 2:29 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] equest crashing on chilled water loop
primaryselection
I am having an issue with equest crashing. The error is associated with
the subtype being secondary for the chilled water loop, however, when I
switch it back to primary, I immediately get kicked out of equest. I
have attached the screenshot of equest and the chilled water loop
appears to be nested. I am not sure how this exactly happened, I was
attempting to redefine the chilled water loop. Here is the excerpt from
the bdl file. Is there any way to edit outside of equest interface so I
can alleviate the crashing??
*3099 * "Chilled Water Loop" = CIRCULATION-LOOP
*3100 * TYPE = CHW
*3101 * SUBTYPE = SECONDARY
*3102 * LOOP-DESIGN-DT = 15
*3103 * SIZING-OPTION = PRIMARY
*3104 * PIPE-HEAD = 55
*3105 * PRIMARY-LOOP = "Chilled Water Loop"
*3106 * LOOP-OPERATION = DEMAND
*3107 * DESIGN-COOL-T = 45
*3108 * COOL-SETPT-CTRL = FIXED
*3109 * LOOP-PUMP = "CHW Loop Pump"
*3110 * HEAD-SETPT-CTRL = FIXED
*3111 * HEAD-SETPT = 30
*3112 * ..
*ERROR******************************************************************
**********************
*ERROR*****Chilled Water Loop cannot be specified as a PRIMARY-LOOP due
to
incorrect SUBTYPE; valid PRIMARY-LOOP must have a SUBTYPE of
PRIMARY
Thanks!
Robert G. Chronic
Cx Team Leader
Energy Solutions Group
E M C Engineers, Inc.
Eaton's Electrical Services & Systems
408 West University Avenue, Suite 402
Gainesville, FL 32601
tel: +1 352 327-9358 ext. 300
mobile: +1 352 275-7417
fax: +1 352 327-9358
RobertGChronic at eaton.com
www.eaton.com <http://www.eaton.com/> /energysolutions
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101220/af7c7fe7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 39998 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101220/af7c7fe7/attachment.jpeg>
More information about the Equest-users
mailing list