Hi Zhiren,
If I were in your shoes, it makes more sense to me to apply option 2 to your
project. Where the retail/commercial is distintly different than the
residential, and I assume that you are applying the different operating
schedules to the respective building types, this seems to offer the most
realistic baseline comparison for your proposed design model.
I suggest you use Option 2.
Cheers,
Pasha
On Tue, Dec 14, 2010 at 7:18 PM, zhiren zhou <zhouzr at cabr-sh.com> wrote:
> Dear all:
>
> My project is a 84- floor super-high building with 27 floors for
> office and 47 floors for residential(hotel and apartment) and others for
> retail and equipment floors. When I select baseline HVAC system I’m confused
> as both the two option below sounds rational:
>
> 1) The Note under TABLE G3.1.1A- Baseline HVAC System Types in Page
> 181 of ASHRAE 90.1 tells that : “Where attributes make a building eligible
> for more than one baseline system type, use the predominant condition to
> determine the system type for the entire building.”
>
> 2) The explanation in Page G-23 of ASHRAE 90.1 MANUAL tells that :
> “If a building has both residential and nonresidential spaces with their
> total conditioned floor area both greater than 20,000 ft², for instance a
> residential tower with retail and restaurants at the base, then the HVAC
> system type is determined separately for the residential and nonresidential
> portions.”
>
> So if I follow option 1 I should select PTAC for the whole building which I
> think unsuitable. else if I follow option 2 I should select PTAC for
> residential and VAV for office and others.
>
> Which option should I follow?
>
> Could anyone tell me? Thanks
>
>
>
> Zhiren ZHOU
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>