[Equest-users] Exterior Lighting
Nick Caton
ncaton at smithboucher.com
Wed Dec 15 11:30:53 PST 2010
The phrasing is a little off for the wizard approach...
If you want to enter the exterior lighting wattage prior to detailed
edit and not have to correct it after the fact, divide the sum of the
installed exterior watts by the square footage of the shell you are
entering the W/SF value in (the exact area to use for this is displayed
on the 2nd shell screen). Enter that W/SF figure in only one shell if
you have multiples.
If you follow that, you'll have the exact installed watts entered
correctly.
Total exterior area lit does not come into the equation.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brian
Fountain
Sent: Wednesday, December 15, 2010 12:49 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Exterior Lighting
You can do that -- or wait and add as a direct load to the electric
meter in detailed edit mode (which is what the wizard is going to do
anyway).
On 12/15/2010 12:37 PM, Lisa Li wrote:
Dear All,
How should we modle the exterior lighting? If I know the total exterior
lighting wattages, should I divide the total outdoor area to get watt /
sq ft for wizard screen 23 inputing?
Thanks,
Lisa Li
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1170 / Virus Database: 426/3317 - Release Date: 12/15/10
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101215/80355308/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101215/80355308/attachment.jpeg>
More information about the Equest-users
mailing list