[Equest-users] boiler and chiller serving multiple buildings
John Aulbach
jra_sac at yahoo.com
Wed Dec 8 09:05:17 PST 2010
Yehuda:
Yes, you certainly can have those seven shells. But you will also have the
eighth shell where the central plant is. eQuest does not care where the plant
is, but what is connected to it. Do no concern yourself with where the plant
resides, but what is connected to it.
BTW, does the plant have its own electric and gas meters? You can worry about
what meters go to what buildings in the Detailed Edit Mode, if you are trying to
match bills.
This sounds like an interesting project, such as a campus or hospital complex.
John
________________________________
From: Yehuda Israel <Yehuda at NewSource-Energy.com>
To: John Aulbach <jra_sac at yahoo.com>; eQuest
<equest-users at lists.onebuilding.org>
Cc: bfrank at newsource-energy.com; Hanan Waizman <hanan at newsource-energy.com>;
howard at newsource-energy.com
Sent: Wed, December 8, 2010 7:25:27 AM
Subject: RE: [Equest-users] boiler and chiller serving multiple buildings
John
Thank you for your help.
I have a question on what you said. The boiler and chiller that service the
eight buildings are extremely big. Anyway I have to start the model in the DD
Wizard. If I make eight different shells and show seven buildings without a
boiler or chiller, it seems that I could
From:John Aulbach [mailto:jra_sac at yahoo.com]
Sent: Tuesday, December 07, 2010 7:06 PM
To: Yehuda Israel; eQuest
Cc: bfrank at newsource-energy.com; Hanan Waizman; howard at newsource-energy.com
Subject: Re: [Equest-users] boiler and chiller serving multiple buildings
Yehuda:
I surmise that all eight buildings are on the central plant with the chillers
and boilers you describe. eQuest doesn't know that your 8 buildings are separate
buildings, just more zones. I would describe your zones (in the Detailed Edit
mode) such as "Building 1-North Zone" or "Building 8-Lobby" and put all the
zones on one massive CHW and HHW loop.
You can also make these loops Secondary loops, if the Central Plant has its own
loops.
Have fun !!
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
PartnerEnergy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com
________________________________
From:Yehuda Israel <Yehuda at NewSource-Energy.com>
To: eQuest <equest-users at lists.onebuilding.org>
Cc: bfrank at newsource-energy.com; Hanan Waizman <hanan at newsource-energy.com>;
howard at newsource-energy.com
Sent: Tue, December 7, 2010 8:46:42 AM
Subject: [Equest-users] boiler and chiller serving multiple buildings
To all:
I have a building complex consisting of 8 buildings. In one of the buildings
are the boiler and chiller that service all of the building through various
pipes. The other buildings don’t have their own boiler and chiller. How do I
model this into eQuest?
Thank you.
Yehuda Israel,
Energy Analyst
New Source Energy Group, Inc.
8 Ellington Way
Main: (845) 445-0457
Fax: (845) 354-6347
www.NewSource-Energy.com
New Hempstead, NY 10977
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101208/0acbef80/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1535 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101208/0acbef80/attachment.jpeg>
More information about the Equest-users
mailing list