[Equest-users] balcony
Brian Fountain
bfountain at greensim.com
Mon Dec 6 11:45:18 PST 2010
In screen 4 of 25 of the DD shell wizard you can specify "Slab
Penetrates Wall Plane" (check box). If you do, eQUEST created a new
wall type of height equal to your slab thickness and composed of 1' of
concrete plus any slab edge insulation you specify on the same wiz
screen. That provides a parallel path for the heat transfer from the
balcony or slab edge. Not exactly 2D heat transfer modelling -- but at
least you aren't ignoring the effect of the slab edge or balcony.
On 12/5/2010 8:43 PM, Shinn, Kim wrote:
>
> Unless the balcony is an extension of the floor slab -- at which point
> it becomes a heat transfer fin. Not too bad if you are in Florida. A
> wreck if you are in Duluth.
>
> And no, I haven't the vaguest idea of how that is modeled.
>
> *Kim E Shinn, PE, LEED AP BD+C, CxA***
>
> /Senior Sustainability Consultant/
>
> (/Direct: 615.346.1902/
>
> (/Mobile: 615.394.4297/
>
> *From:*Nick Caton [mailto:ncaton at smithboucher.com]
> *Sent:* Friday, December 03, 2010 1:53 PM
> *To:* John Aulbach; damla kaplan; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] balcony
>
> Agreed -- exterior balconies are nothing more complicated than shades.
>
> Repeating balconies as seen commonly with multistory apartment
> buildings & hotels should be defined as typical window overhangs in
> the wizards of the appropriate dimensions. If it's more of an
> isolated case you might save time creating a single building shade in
> detailed edit instead.
>
> ~Nick
>
> cid:489575314 at 22072009-0ABB**
>
> **
>
> *NICK CATON, E.I.T.***
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com__
>
> *From:*equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *John Aulbach
> *Sent:* Friday, December 03, 2010 12:57 PM
> *To:* damla kaplan; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] balcony
>
> Do you mean an outdoor balcony? I would add a shading device over a
> window on the floor below.
>
> John R. Aulbach, PE, CEM
>
> Senior Energy Engineer
>
> ------------------------------------------------------------------------
>
> *Partner****Energy***
>
> 1990 E. Grand Avenue, El Segundo, CA 90245
> W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
>
> www.ptrenergy.com <http://www.ptrenergy.com/>| jaulbach at ptrenergy.com
> <mailto:%7C%20jaulbach at ptrenergy.com>
>
> ------------------------------------------------------------------------
>
> *From:*damla kaplan <kaplan.damla at gmail.com>
> *To:* equest-users at lists.onebuilding.org
> *Sent:* Fri, December 3, 2010 10:34:06 AM
> *Subject:* [Equest-users] balcony
>
> How can i add balcony to buildings at equest?
>
> --
> ~õkyanus~
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> No virus found in this message.
> Checked by AVG - www.avg.com <http://www.avg.com>
> Version: 10.0.1170 / Virus Database: 426/3299 - Release Date: 12/05/10
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101206/1a3c7e1e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101206/1a3c7e1e/attachment.jpeg>
More information about the Equest-users
mailing list