[Equest-users] Roof Reflectiveness / Absorbency for cool roof
    Bishop, Bill 
    wbishop at pathfinder-ea.com
       
    Mon Dec  6 11:10:13 PST 2010
    
    
  
Rob,
 
When I model cool roofs using ASHRAE Standard 90.1 Appendix G, I change
the absorptance of the roof construction to 0.55, per the
reflectance=0.45 allowance in Table G3.1. Energy savings may be modest,
or even negative, depending on several factors, including climate, roof
U-value, and electric-vs.-gas/heating energy rates. There are good
discussions in the archives regarding the nuances of cool/white roofs.
 
Regards,
Bill
 
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
 
 134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114            F: (585) 325-6005
wbishop at pathfinder-ea.com           www.pathfinder-ea.com
<http://www.pathfinder-ea.com/> 
P   Sustainability - the forest AND the trees. P 
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob
Hudson
Sent: Monday, December 06, 2010 1:58 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Roof Reflectiveness / Absorbency for cool roof
 
i am trying to model a cool roof by changing the absorbency from 0.7 to
0.55.  it is the right approach? i am getting an increase in energy
costs, which goes against logic.
-- 
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101206/62dc7a09/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101206/62dc7a09/attachment.jpeg>
    
    
More information about the Equest-users
mailing list