[Equest-users] LEED Question: Outdoor air intake flow for a VAV system..
Omar Katanani
omar at ecoconsulting.net
Wed Dec 1 10:33:06 PST 2010
Thanks Maryanne!
By reading through 62.1 2007 section 6.2.5 (Ventilation rate procedure for Multiple Zone Recirculating Systems), a detailed procedure is given to calculate the Outdoor design air flow for each Air Handling Unit Vot.
This Vot is, as you said, greater than the sum of each zone's outdoor rate.
The question is:
How do I correct each zone's outdoor air rate?
A possible simple way is to check the ratio of Vot divided by the sum of each zone's outdoor rate. Assume this number is, lets say, 1.1
I can then multiply each zone's outdoor air by this ratio (1.1) to get the new corrected value.
This is a proposed method based on some logic.
Any suggestions?!
Thanks!
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel: +961 (0) 1 971 266
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0)207 939 0989
Fax: +44 (0)207 939 0981
Website: www.ecoconsulting.net
-----Original Message-----
From: Maryanne Mason [mailto:maryanne.mason at ausencosandwell.com]
Sent: Wed 12/1/2010 7:46 PM
To: Omar Katanani
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] LEED Question: Outdoor air intake flow for a VAV system..
Hi Omar
Based on ASHRAE Std 62.1, the total outside air must be calculated at the
system level. If you then take the fraction of outside air supplied to the
system and multiply it by your system flow to each zone, you will get the
total outside air supplied to the zone.
However, if you are trying to calculate the outside air requirements of the
zone, you need to calculate the space and occupancy requirements based on
the zone type (IE [# of occupants] * [cfm/occupant] + [square footage] *
[cfm / sq ft]), and then divide them by the ventilation effectiveness (IE
0.8 when supplying hot air from ceiling diffusers).
Please note that the total outside air required at system level is not the
sum of the individual zone requirements.
If you wish to get more information on this calculation, you can use the
following link:
http://www.ashrae.org/technology/page/132
and click on the standard 62.1-2001 addenda link. Then download addendum
"n".
This addendum has a good explanation of how the calculations should be done.
(Some of the occupancy tables have been updated since the addendum was
published, but the calculation method is still valid).
I hope I have clarified this issue somewhat.
Regards,
MaryAnne Mason
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar
Katanani
Sent: Wednesday, December 01, 2010 2:51 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED Question: Outdoor air intake flow for a VAV
system..
Dear all,
I have a LEED related question and I'd appreciate it if someone could help!
The LEED Reference guides show the method to calculate the outdoor air
intake flow (Vot) for the multiple-zone system (VAV). This Vot is for the
whole <http://www.leeduser.com/glossary/14#term4654> AHU. How can I find
the Vot for each zone separately?
Many thanks!
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel: +961 (0) 1 971 266
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 207 939 0989
Fax: +44 (0) 207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101201/145deab0/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 27542 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101201/145deab0/attachment.jpg>
More information about the Equest-users
mailing list