[Equest-users] Geothermal Well Field Modeling

Dan Russell danr at engineeringinc.com
Thu Apr 29 09:34:50 PDT 2010


Hi All - I am wondering if anyone has much experience with the geothermal well field capabilities of eQUEST, in particular with vertical well fields.  I am concerned about the accuracy of the calculation methodology for the vertical well fields, primarily due to a large discrepancy we are getting between the eQUEST results and the results of a separate geothermal well field software produced by Gaia Geothermal.  Here are the parameters:

Vertical well field
Ground conditions & well field dimensions are identical in both eQUEST and Gaia simulations.
Equest model has four 4x5 rectangular well fields (80 bore holes total) with 200 ft bore depth.  Plant report PS-C shows that the fourth well field has no load, thus using at most 60 of the 200 ft wells.
Gaia software inputs load data from the DOE2 report SS-I for each zone along with the matching heat pump size (specific to manufacturer) selected for the project for the zone.  This software uses its knowledge of the heat pump performance to generate the required well-field size and depth.  The result is 120 well fields of 250 ft bore depth or 80 well fields of 350 ft bore depth.

I would expect some discrepancy between different software, but in this case the eQUEST simulation is using only about 50% of the required well-field size calculated by the Gaia software.  The Gaia calculation is coming out much larger than what the owner and design-build contractor had planned for.

How reliable is the eQUEST simulation on vertical well-fields?

I believe the primary difference is that Gaia software uses "real" manufacturer performance data for heap pump models specified and eQUEST uses PVVT system with default GSHP performance curves.  Could this difference really make such huge impact on the results?

Thanks in advance for any insight.

Dan Russell
[cid:image001.png at 01CAE784.47A119C0]

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100429/92a2d772/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 29839 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100429/92a2d772/attachment.png>


More information about the Equest-users mailing list