[Equest-users] Demand Controlled Ventilation
    Victor Yeung 
    Victor at invirosystems.ca
       
    Wed Apr 28 09:30:01 PDT 2010
    
    
  
Hello all,
 
I also have a similar question related to minimum OA settings for DCV,
particularly with OA-FLOW/PER and OA-FLOW/AREA.  Say I am using ASHRAE
62.1 for my OA rates, there are minimum requirements for cfm/person and
cfm/area.  However, the way eQuest calculates min zone OA is by taking
the higher value of either OA-FLOW/PER or OA-FLOW/AREA, not the combine
total.  To correctly model the OA requirement, I have to calculate the
combine OA rate (i.e. {[cfm/per * max # of person] + [cfm/area * floor
area] } / floor area) and input that value in OA-FLOW/AREA.  Now, the
problem comes in when we include DCV into the model, at which eQuest
cannot calculate the savings because the OA-FLOW/PER value is not
entered.  I would greatly appreciate it if anyone can clarify this.
 
VICTOR YEUNG, BASc, LEED(r) AP
EIT - LEED(r)/Sustainable Development
victor at invirosystems.ca <mailto:victor at invirosystems.ca> 
 
 
From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com] 
Sent: April 28, 2010 11:16 AM
To: Rob Hudson
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Demand Controlled Ventilation
 
Rob,
 
You need to set up an hourly report. See attached.
 
Bill
 
________________________________
From: Rob Hudson [mailto:rdh4176 at gmail.com] 
Sent: Wednesday, April 28, 2010 11:06 AM
To: Bishop, Bill
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Demand Controlled Ventilation
 
How can i tell if the system is using a lower OA CFM during the less
occupied times? 
On Wed, Apr 28, 2010 at 10:43 AM, Bishop, Bill
<wbishop at pathfinder-ea.com> wrote:
Rob,
 
I recently modeled DCV successfully for the first time. (I showed
savings anyway.) You need to enter zone-level OA as OA-FLOW/PER and/or
OA-FLOW/AREA. The OA flow/per (person) is what will get you the savings,
based on your occupancy schedule(s). I also created a MIN-AIR-SCH,
coinciding with the fan schedule, set to zero when fan is off and -999
when fan is on.
 
Regards,
Bill
 
William Bishop, EIT, BEMP, LEED(r) AP | Pathfinder Engineers &
Architects LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www..pathfinder-ea.com <http://www.pathfinder-ea.com> 
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob
Hudson
Sent: Wednesday, April 28, 2010 9:55 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Demand Controlled Ventilation
 
I am having some trouble with setting up DCV in my model.  if i select
DCV in Zone Sensors for the Min OA Control Method and a min outside Air
Ratio, do i need any Zone level OA inputs?
Any help or insight as to what inputs are necessary for DCV would be
great!
-- 
Rob Hudson
-- 
Rob Hudson