[Equest-users] Lab Space ACH

Matthew Dubrovich mdubrovich at emcengineers.com
Fri Apr 23 09:19:17 PDT 2010


Hi Rob,

Remember that zone level OA inputs override system level OA inputs.  Check if you're changing a system level input in the parametric run that is being ignored due to the 12 ACH OA value set at the zone level.

Matt Dubrovich, P.E.
LEED AP

EMC Engineers, Inc.
www.emcengineers.com<http://www.emcengineers.com/>
Making buildings work.  Better.
(303) 974-1217 - direct
(720) 279-4426 - mobile
(303) 974-1239 - fax

Confidentiality Notice: This message and any materials attached are confidential, and are intended solely for the use of the addressee. If you are not the intended recipient, be advised that unauthorized use, disclosure, copying, or distribution is strictly prohibited. If you received this message in error please notify the sender and destroy your copy immediately.

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob Hudson
Sent: Friday, April 23, 2010 9:51 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Lab Space ACH

I have a large 4 story building that i am modeling that is about 50 % lab space set to 12 ACH and 100% OA and constant volume.  I have created a parametric run to turn down to 6 ACH and i am getting the same CFM and utility bill information.  Is there something i might be missing as an input to either the model or the parametric run?

any help is greatly appreciated,

--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100423/abfbc313/attachment.htm>


More information about the Equest-users mailing list