Michael,
Try this:
Under Air-Side System HVAC Parameter, Supp Heat/Defrost, try entering a
really low number for the HP Supp Heat Capacity, on the order of .001 Btuh
or so.
Carol
On Thu, Apr 22, 2010 at 7:58 AM, M. Shields <mshields at fstrategies.com>wrote:
>  Fellow eQuesters,
>
>
>
> I am trying to model a building using heat pumps, however, there will be no
> backup heaters in the building.  Is there a way to disable this from the
> model?  When I ran the wizard I selected the heating source was  “DX Coils
> (Heat Pump)” but when I go through the reports there is consumption for “HT
> Pump Supplem”.
>
>
>
> Thanks,
>
> Michael
>