[Equest-users] Thermal Mass Wall and R-Value

Rob Hudson rdh4176 at gmail.com
Thu Apr 22 09:30:17 PDT 2010


That is the answer i was expecting to here.  thanks for your input

On Thu, Apr 22, 2010 at 12:27 PM, Bruce Easterbrook <bruce5 at bellnet.ca>wrote:

>  That doesn't sound right.  Poured concrete has an R-value around
> 0.08/inch.  When "effective" is used commercially it normally is a hocus
> pocus addition for the mass effect but shouldn't be much more than 10%.
> eQuest would calculate it as a lag effect based on the mass, so a steady
> state value would be most appropriate.
> Bruce Easterbrook
>
>
> On 22/04/2010 10:38 AM, Rob Hudson wrote:
>
> When creating a model, i noticed that the R-value of the concrete i am
> using is the "effective" R-value, rated at 22.  Should i use this or should
> i ask the concrete manufacturer for a steady-state R-value which will be
> much more accurate based on the materials?
>
> --
> Rob Hudson
>
>
> _______________________________________________
> Equest-users mailing listhttp://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100422/1e9a33a6/attachment.htm>


More information about the Equest-users mailing list