[Equest-users] LEED demand numbers
Dakota Kelley
dakotak at teliospc.com
Wed Apr 21 09:02:03 PDT 2010
Austin,
The LEED template is requesting demand by end-use, so non-coincident is what you should be reporting; it is each particular end-use’s peak demand. If there is exterior lighting consumption, there should be a corresponding non-zero peak demand regardless of what time the peak occurs. I’m not sure what report is showing zero exterior lighting demand, but it’s possibly due to a very low peak and eQUEST is simply rounding down. Or, as Otto stated, you might be looking at peak demand for a daytime hour. Regardless, the LEED template should not show annual consumption with zero peak demand for any end-use. It might only be 0.1 kW, but there must be demand for there to be consumption.
The LEED reviewers are using peak demand as a sanity check for the connected power listed elsewhere in the template (i.e. Table 1.4 in v2.2). For example, if total connected fan power on a VAV system is reported as 100 kW but the ventilation fan end-use shows a peak demand of only 25 kW, then it is obvious something is wrong. The implication is that the fans are grossly over-sized and don’t operate above ~25% capacity. Likewise, if peak demand for the same fans is reported as 120 kW, then we apparently have magic fans that peak 20% beyond their physical limits. So, just make sure demand is roughly in agreement with the peak connected power listed for a given end-use.
Thanks,
DAKOTA KELLEY
Project Designer
Office: 214-744-6199
Cell: 214-280-3825
Fax: 214-744-0770
http://www.teliospc.com <http://www.teliospc.com/> 3535 Travis St. Suite 115
dakotak at teliospc.com <mailto:dakotak at teliospc.com> Dallas, TX 75204
| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed,
And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you
are not the intended recipient, please email the sender immediately, and delete this email from all computers. Any
distribution or other use is strictly prohibited. Copyright © 2010 Telios Corporation.
From: Otto Schwieterman [mailto:oschwieterman at fhai.com]
Sent: Wednesday, April 21, 2010 9:53 AM
To: Austin Hermsen; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] LEED demand numbers
The exterior lighting should have a demand of zero. The peak demand time is almost always during the day and the exterior lights are off during the day. Simply write a short narrative explaining this and they will accept your answer.
From: Austin Hermsen [mailto:ahermsen at enermodal.com]
Sent: Wednesday, April 21, 2010 10:48 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED demand numbers
Which value do you usually use for the demand number in the LEED templates. I have been using the coincident demand value but that yields a value of zero for exterior lighting (which always gets a comment from LEED). Should I be using the non-coincident value?
________________________________________________________________________________________
Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
designated individual or entity. If you received this message in error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe unlawful. Any information included in
this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100421/df33ae16/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3170 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100421/df33ae16/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2327 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100421/df33ae16/attachment.jpeg>
More information about the Equest-users
mailing list