[Equest-users] HP and DOAS
James Hansen
JHANSEN at ghtltd.com
Tue Apr 13 07:50:35 PDT 2010
There are a bunch of issues that could potentially be causing your
results - we'd need the .inp and .pd2 files to be able to troubleshoot.
Off the bat, if your DOAS system shows zero loads, then it sounds like
you need to make sure there is a fan schedule for the DOAS system, the
actual fan CFM is specified, and the dummy zone has a heating/cooling
thermostat roughly matching the supply temps of the DOAS system.
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Caleb
Bulow
Sent: Tuesday, April 13, 2010 10:38 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] HP and DOAS
I really need some help ASAP on this.
I have a geothermal HP system and am comparing it to an air-2-air HP
system, per ASHRAE 62.1. My cooling energy usage on the GSHP's are
significantly higher than the air-2-air HP and this despite higher EER
for the GSHP. Why is this? Is there some pumping being added into the
GSHP? It appears the pumps are separate on the Monthly Energy
Consumption report.
I am set up a DOAS and each HP receives its fresh air from the DOAS
system, yet the DOAS shows zero loads for cooling and heating in the
SS-A System Loads Summary report. This despite the warning I have in
the ATTN report that the System DOAS may have inadequate cooling
capacity. The summary report shows the full amount of CFM for the DOAS,
and also shows the capacity.
Thanks.
Caleb Bulow
PRAIRIE ENGINEERING, P.C.
720 WESTERN AVE
MINOT, ND 58701
P. (701) 852-6363
F. (701) 839-7085
The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee. It is the property of GHT Limited. Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful. If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100413/1d6f01b3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 161 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100413/1d6f01b3/attachment.png>
More information about the Equest-users
mailing list