[Equest-users] Chiller ROI - HELP!
Pasha Korber-Gonzalez
pasha.pkconsulting at gmail.com
Thu Apr 1 13:10:37 PDT 2010
Brett,
to get better part load data and efficiency of your proposed chiller
replacement, call your chill sales engineer and ask them to generate a part
load performance report for you in 10% unloading increments, then you can
see the decrease in performance efficiency for each part-load step of the
chiller. Also be sure that you recognize if you are looking at RATED
Conditions (which means chiller performance at ARI standard conditions), or
at DESIGN conditions (which are your project's specified operating
conditions--this would account for part load efficiencies if you were
running a 12-or 14 Degree delta-T across your chiller.)
Before you set up a new performance curve you will need to get this data
supplied from the manufacturer.
Pasha
On Thu, Apr 1, 2010 at 2:01 PM, James Hansen <JHANSEN at ghtltd.com> wrote:
> KW/ton drops off with decreasing part load, and since the chiller isn’t
> always operating at ARI full load conditions, you can’t just divide total
> chiller energy consumption (in KWH) by the total cooling load (in btu) and
> hope to get anywhere near the full load rated KW/ton.
>
>
>
> As you go about this ROI study, make sure that when you are analyzing your
> proposed chiller replacement, that you create a custom EIR vs PLR curve
> based on manufacturer’s data, otherwise you’re using a default DOE-2 curve
> that isn’t necessarily correct.
>
>
>
> Furthermore, to make the study worthwhile, the existing chiller model
> really needs to be normalized as best as possible to actual building
> operating conditions. You can get away without doing it for a simple
> comparison, but it would be more accurate if you normalized to utility
> bills.
>
>
>
> *GHT Limited
> **James Hansen**, PE, LEED AP*
>
> *Senior Associate***
>
> 1010 N. Glebe Rd, Suite 200
>
> Arlington, VA 22201-4749
>
> 703-338-5754 (Cell)
>
> 703-243-1200 (Office)
>
> 703-276-1376 (Fax)
>
> www.ghtltd.com
>
> * *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Brett Sanicola
> *Sent:* Thursday, April 01, 2010 2:38 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Chiller ROI - HELP!
>
>
>
> I've been attempting to calculate a simple ROI for a new 250 ton chiller
> our client wants to install to replace his older chiller. I ran the
> simulation for the default "high rise hotel" construction which, to my luck,
> is quite similar to the actual building. The detailed results, however, are
> not making sense to me. Specifically, when I look at Equipment Loads and
> Energy Use for the Chiller, the Elec Use and Cool Load don't coincide given
> the default Chiller efficiency of .67kw/ton. For example they give a
> Chiller Elec Use of 535453 KWH and a Cool Load of 3294 MBTU. However,
> according to my calculations, at .67KW/TON, 535453 KWH should give me closer
> to 9590 MBTU. I see most of the hours are in part load range, but does the
> efficiency drop off that dramatically at part load that it would explain the
> discrepancy? Which numbers should I base my analysis on, the Cool Load
> number or the Elec Use number.
>
>
>
> Also, on the same page (Equipment Loads and Energy Usage), it gives me a
> peak load of 2436 KBTU/HR. However, when I go to the section titled
> "Building Peak Load Components" the peak cooling load is significantly less
> (1619 KBTU/HR)
>
>
>
> At this point, I have no idea what any number represents, since I don’t
> know how it was calculated.
>
>
>
> I greatly appreciate any help! Thanks.
>
>
>
> Respectfully,
>
>
>
> Brett Sanicola
>
> Engineer
>
> ASB Engineering
>
> (516) 785-4200
>
> ------------------------------
> The information contained in this communication is confidential, may be
> privileged, and is intended only for the use of the addressee. It is the
> property of GHT Limited. Unauthorized use, disclosure or copying of this
> communication or any part thereof is strictly prohibited and may be
> unlawful. If you have received this communication in error, please notify
> me immediately by return e-mail or by e-mail to ght at ghtltd.com, and
> destroy this communication and all copies thereof, including all
> attachments. Thank you.
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100401/e1dad014/attachment.htm>
More information about the Equest-users
mailing list