[Equest-users] Auto Garage Ventilation Rate

Ahmed Azhari aazhari at jainconsultants.com
Thu Apr 1 08:18:24 PDT 2010


My reference building is in accordance with Model National Energy Code of
Canada for Buildings 1997 MNECB. It makes sense to me to treat the
ventilation rate the same as the reference in an auto garage. This way
process ventilation is accounted neutral in both cases.    

 

Thanks,

 

Ahmed

 

 

From: Nick Caton [mailto:ncaton at smithboucher.com] 
Sent: Thursday, April 01, 2010 11:03 AM
To: aazhari at jainconsultants.com; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Auto Garage Ventilation Rate

 

Hello Ahmed,

 

It's unclear whether your baseline/reference building is intended to follow
the guidelines of 90.1 or some other modeling standard by your Ministry.
ASHRAE 90.1 in any case tells us proposed and baseline buildings must have
the same minimum ventilation rates (G3.1.2.5) - so under that guidance, I
would set the same CFM/ft2 for each model.

 

~Nick

cid:489575314 at 22072009-0ABB

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ahmed
Azhari
Sent: Thursday, April 01, 2010 9:54 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Auto Garage Ventilation Rate

 

Hello Equesters,

 

In a case where we have an Auto Repair garage where the minimum ventilation
rates set by local code (i.e. Ministry of Labour) is greater than what the
reference building would use, is it adequate to modify the reference
building ventilation rate to match that of the proposed. 

 

In my case the ventilation rate in this Auto Repair garage is 2cfm/ft2 and
for the reference it would be 0.7cfm/ft2.

 

I appreciate any help.

 

__________________________________________________________________________

Ahmed Azhari, B.Eng., LEEDR AP

Energy Analyst

 

Jain Sustainability Consultants Inc.

 

2260 Argentia Road, 2nd Floor

Mississauga, Ontario L5N 6H7, CANADA

Tel:  (905) 542 7211 Ext 234

Fax: (905) 542 7622

Email:  <mailto:aazhari at jainconsultants.com> aazhari at jainconsultants.com

Web:  <http://www.jainassoc.com/> www.jainassoc.com

 

NOTICE OF CONFIDENTIALITY
This communication, including any attachments, is intended only for the use
of the addressees and is confidential. 

If you received this communication in error, please permanently delete the
entire communication from any computer or other storage medium.

 

cid:image002.gif at 01C92EB4.ADAA2610Please consider your environmental
responsibility before printing this e-mail & any documents

 



__________ Information from ESET Smart Security, version of virus signature
database 4992 (20100401) __________

The message was checked by ESET Smart Security.

http://www.eset.com



__________ Information from ESET Smart Security, version of virus signature
database 4992 (20100401) __________

The message was checked by ESET Smart Security.

http://www.eset.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100401/a4c81c7e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100401/a4c81c7e/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1257 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100401/a4c81c7e/attachment.gif>


More information about the Equest-users mailing list