The other thing to consider is that DOE-2 forces an air balance in every
zone. If the zonal (local) exhaust is less that the OA delivered then the
balance is exhausted at the central system exhaust.
In terms of heat recovery, only air exhausted at the central unit is
available for heat recovery. By specifying zonal exhaust, that exhaust
flow rate is not passed through the heat recovery device (if specified).
> Sambhav:
>
> If you want Exhaust CFM Fan energy, then I believe you need to specify
> Exhaust CFM.
>
> OK, eQuesters, I think I have this straight. If you specify an Exhaust CFM
> LESS THAN OSA CFM, nothing airwise changes, and Exhaust CFM translates to
> an Exhaust fan HP. If Exaust CFM EXCEEDS OSA CFM, the OSA CFM is increased
> to account for no negative airflow. And Exhaust CFM STILL creates and
> Exhaust HP.
>
> Comments from our studio audience, please..
>
>
>
>
> ________________________________
> From: sambhav tiwari <tiwari.sambhav at gmail.com>
> To: equest-users at lists.onebuilding.org
> Sent: Wed, March 31, 2010 10:47:32 PM
> Subject: [Equest-users] Air side HVAC
>
> Hi All,
> In the AIR side HVAC under zone when we go to outdoor air
> tab there it asks about exhaust fan cfm for each zone so do we have to
> specify it exhaust cfm zonewise or the program assumes it that what ever
> is the fresh air cfm for each conditioned zone same will be the exhaust
> cfm.
>
> Any response will be appreciable.
>
> Thanks
> Sambhav Tiwari.
>
>