[Equest-users] Adding Cupola to one story building

Nick Caton ncaton at smithboucher.com
Mon Sep 28 16:20:23 PDT 2009


What you may need to do, to account for varying exterior roof heights
within the same floor level, is define two "shells" of different
heights.  Attached is a quick mspainting masterpiece by yours truly
attempting to illustrate how I've done this for other projects.  If you
define your shell perimeters in a way that the yellow-circled vertices
are shared between the two zones, the resulting "shared" walls will
merge and correctly identify one zone adjacent to the other, if I recall
correctly.  The orange-circled vertices for "zone 1" however would need
to be separated a nominal distance apart (like 1-inch) to allow you to
define it.  This requires some careful pre-planning in your custom
footprint file for importing.  I used this strategy heavily for a
project with a lot of monitors inside the building for daylighting.

 

On the other hand, your situation may be easier to deal with if you're
truly talking about simply varying the ceiling height of one or more
zones (not the roof height).  Individual space/plenum heights are
modifiable from the detailed mode spreadsheets. 

 

~Nick

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Heather
Bird
Sent: Friday, September 25, 2009 5:34 PM
To: Subject: [Equest-users] Adding Cupola to one story building

 

I am a new user of eQuest. I have entered a one story building in eQuest
by building a custom Footprint Shape (imported CAD drawing). The
building has a raised ceiling in one area. I cannot see a way to account
for the difference in height other than doing some sort of wall height
averaging calculation. Is there a feature I am overlooking to help me
indicate the raised ceiling in one location? I am in CA and using
version 3.60, build 5210. Please let me know if this is the most current
version for Title 24 as well. Thank you.

 

Heather Bird
Meline Engineering Corporation
P.O. Box 276665
Sacramento, CA 95827

 

Office:  9216 Kiefer Blvd, Suite 6
              Sacramento, CA  95826

 

Phone:  (916) 366-3458
Fax: (916) 366-3958

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090928/30116e26/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090928/30116e26/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: HOWTOGET2HEIGHTS.JPG
Type: image/jpeg
Size: 27205 bytes
Desc: HOWTOGET2HEIGHTS.JPG
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090928/30116e26/attachment-0001.jpeg>


More information about the Equest-users mailing list