[Equest-users] Humidifier Loads

Grando, John JGrando at cosentini.com
Wed Sep 23 11:13:48 PDT 2009


You can specify an hourly output for each air handler.

go to the "Project and Site" tab, click on "Hourly Report Blocks" and create a block that looks like the picture below.  Don't forget to add the hourly report BLOCK to the hourly report SCHEDULE before you run your simulation.  I think this will work but I have not tried it myself.  Good luck

[cid:940141318 at 23092009-1317]


John Grando LEED AP| Mechanical Engineer





________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason.Stevens at tac.com
Sent: Wednesday, September 23, 2009 11:37 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Humidifier Loads

I have air handlers with steam humidifiers.  Does anyone know where to find the humidifier loads (lbs/hr) in the detailed output file?

Thanks,
Jason Stevens, EIT
Engineer II

TAC
Energy Solutions
4431 North Front Street Suite 100
Harrisburg, PA 17110 USA

Email:    Jason.Stevens at tac.com

P As part of our commitment to the environment, please do not print this email unless necessary. Thank you.



NOTICE OF CONFIDENTIALITY

This E-mail message and its attachments (if any) are intended solely for the use of the addressees hereof.  In addition, this message and the attachments (if any) may contain information that is confidential, privileged and exempt from disclosure under applicable law.  If you are not the intended recipient of this message, you are prohibited from reading, disclosing, reproducing, distributing, disseminating or otherwise using this transmission.  Delivery of this message to any person other than the intended recipient is not intended to waive any right or privilege.  If you have received this message in error, please promptly notify the sender by reply E-mail and immediately delete this message from your system.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090923/d253f4cb/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook.jpg
Type: image/jpeg
Size: 81253 bytes
Desc: Outlook.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090923/d253f4cb/attachment.jpg>


More information about the Equest-users mailing list