[Equest-users] G.3.1.2.8 Design Air Flow
Dakota Kelley
dakotak at teliospc.com
Fri Sep 18 09:44:06 PDT 2009
…and to follow up on what Vikram said, eQUEST is sizing flows off the system SA temp and each zone’s indoor design temperatures. Indoor design temps do not necessarily correspond to the settings in the thermostat schedule; users need to verify both. The screen below is where you specify design temps. The spreadsheet view is helpful for adjusting all zones quickly:
DAKOTA KELLEY
Project Designer
Office: 214-744-6199
Cell: 214-280-3825
Fax: 214-744-0770
http://www.teliospc.com <http://www.teliospc.com/> 3535 Travis St. Suite 115
dakotak at teliospc.com <mailto:dakotak at teliospc.com> Dallas, TX 75204
| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed,
And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you
are not the intended recipient, please email the sender immediately, and delete this email from all computers. Any
distribution or other use is strictly prohibited. Copyright © 2009 Telios Corporation.
From: Vikram Sami [mailto:VSami at lasarchitect.com]
Sent: Thursday, September 17, 2009 5:09 PM
To: Robby Oylear; Chan, Walter; Equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] G.3.1.2.8 Design Air Flow
To follow up on what Robb said, the fan delta T is the heat gain across the fan from the fan motor.
You input your supply air temperature in this window:
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Robby Oylear
Sent: Thursday, September 17, 2009 5:53 PM
To: 'Chan, Walter'; Equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] G.3.1.2.8 Design Air Flow
The delta T G.3.1.2.8 is referring to a 20 degree delta between room cooling setpoint and supply air temperature. For example:
Room Cooling Setpoint = 75 °F
20 °F delta from G.3.1.2.8 = -20 °F
Supply Air Temperature = 55 °F
A 20 degree fan delta T would be a MONSTER of a fan..
Robby Oylear, LEED® AP
Mechanical Engineer
direct: 206.788.4571
cell: 206.354.2721
www.rushingco.com <http://www.rushingco.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chan, Walter
Sent: Thursday, September 17, 2009 2:50 PM
To: Equest-users at lists.onebuilding.org
Subject: [Equest-users] G.3.1.2.8 Design Air Flow
When I use delta T 20F for supply fan, the CFM stays the same and the cooling load is up 60% and heating load is slightly lower. Any clue?
Is there a correct way to put in the Delta T 20F (after I set default and not using fan static pressure) and eQuest will calculate the correct CFM?
Thanks for the help.
Walter W. Chan, P.E., LEED AP
CAS Group
1341 North Delaware Ave., Suite 500 | Philadelphia, PA 19125
T: 215.427.8711 | F: 215.427.8710
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090918/1db85d2f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 24103 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090918/1db85d2f/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3170 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090918/1db85d2f/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 32853 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090918/1db85d2f/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2327 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090918/1db85d2f/attachment-0001.jpeg>
More information about the Equest-users
mailing list