[Equest-users] eQuest Workaround for Water Economizers
    Steven Savich 
    ssavich at systemswestengineers.com
       
    Fri Sep 18 08:38:11 PDT 2009
    
    
  
Tom, 
 
In the equest/DOE new features manual, there's a section on "water
economizer chillers"
 
Basically, to run a cooling tower in water economizer mode, you have to
define a (virtual) water economizer chiller and attach a cooling tower &
condenser water loop to it.  You'll need to set up the water econ chiller,
water econ condenser loop, and water econ cooling tower as  *completely*
separate entities from any other chillers & cooling towers that you run and
have them attached to the primary chilled water loop in parallel with the
other chillers.
 
You also may need to use schedules, equipment controls, and load management
of the chillers and circulation loops depending on your exact plant
configuration.
 
For the water econ info, look under help/DOE2 help/Volume 6: New
Features/Chiller Water Economizer
 
Hope this helps,
Steven
 
Steven Savich, LEED AP
Systems West Engineers
411 High Street
Eugene, OR  97401-2427
(541) 342-7210
(541) 342-7220 (fax)
  _____  
From: Tom O'Brien [mailto:Tom at NorthernArchitects.com] 
Sent: Friday, September 18, 2009 7:56 AM
To: ssavich at systemswestengineers.com
Subject: eQuest Workaround for Water Economizers
 
Steve -
 
I read your eQuest post today today regarding your campus chilled water
system / local cooling tower question.  I'm afraid I don't have a suggestion
as I've not progressed that far with eQuest.
 
However, you noted that "I'm familiar with the equest workaround for water
economizers".  We've been stumped by this in trying to set up a cooling
tower / chiller combination that lets the cooling tower act as a precooler
for the air-cooled chillers and/or as the cooling source when the building
needs cooling in the winter months (our winter months are plenty cold enough
to handle the relatively low cooling needs we have with a cooling tower
without running the chillers).  eQuest doesn't seem to have a way to allow
us to connect both the chillers and the cooling tower to the chilled water
piping.  The typical eQuest cooling tower seems to want to connect to the
condenser water off the chillers and assumes the chillers are water-cooled.
 
Can you point me in the right direction to find the find the workaround you
mentioned?
 
Many Thanks.
 
Tom
Tom O'Brien
Northern Architects, Inc.
207 King Street Suite 3
Burlington, VT 05401
T: 802-658-1953
F: 802-658-2975
E: Tom at NorthernArchitects.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090918/16783c12/attachment.htm>
    
    
More information about the Equest-users
mailing list