[Equest-users] Heating Hours Unmet
Nisonger, Kyle M NWK
Kyle.M.Nisonger at usace.army.mil
Mon Sep 14 08:42:27 PDT 2009
I have assigned each zone it's own single zone system, but I still am coming
up with about the same number of unmet hours. I can manually adjust the
design cfm to lower them, but this seems futile trying to play around with it
to get it just right. Shouldn't eQuest automatically size the equip. and
cfm's to meet the load? Another question I have is why doesn't the percent
of hours outside of the throttling range on the BEPS report match up with the
number of unmet hours on the SS-R report? I have attached my project files
if anyone has time to look at them. I appreciate your help.
Thanks,
Kyle Nisonger
Mechanical Engineer, LEED AP
US Army Corps of Engineers
Kansas City District
(816) 389-3224
-----Original Message-----
From: Jeremy Poling [mailto:jpoling at epsteinglobal.com]
Sent: Sunday, September 13, 2009 11:43 PM
To: Nisonger, Kyle M NWK; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Heating Hours Unmet
Kyle,
Try this first: eQuest expects a single-zone system to serve just that - a
single zone. You'll need to have a separate single zone system created for
each zone you need to assign to that system. Once that is done, eQuest will
then be able to address the thermostats in each zone adequately and you
should see a rather dramatic drop in your unmet heating hours, possibly
eliminating them altogether.
After that, if unmet heating hours remain there are a number of other things
to look at. Let us know if the above works first.
JEREMY R. POLING, PE, LEED AP
Senior Sustainability Analyst
Strategic Services
Site Solutions | Operations | Sustainability
EPSTEIN
Epstein is a firm believer in sustainability. We ask that you please consider
the environment before printing this e-mail.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nisonger,
Kyle M NWK
Sent: Friday, September 11, 2009 4:11 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Heating Hours Unmet
Equesters,
I have a packaged single zone system using DX cooling and Furnace heating
that serves 7 different zones and is controlled by the corridor zone. This
is supposed to replicate "System 3" in ASHRAE 90.1 appendix G. I have many
unmet heating hours (including my system control zone). I have let eQuest
auto size equipment capacities and and cfm. I have tried doing everything I
can think of to reduce the number of unmet hours. My OA volumes are pretty
small and shouldn't be affecting it. I expected possibly a few unmet hours
in some of the zones, but not in my control zone, the corridor, and not to
this magnitude. I get the following warning message seen below, I'm not
sure what it means by "Baseboard-Rating"? Any ideas on what this means or
how I could reduce the number of unmet heating hours?
**WARNING********************************************************************
**
ZONE EL1 Food Storage Zn (G.S2)
might have insufficient heating capability.
Check that the SYSTEM or ZONE HEATING-CAPACITY plus this
ZONEs BASEBOARD-RATING is adequate to maintain the ZONE
specified DESIGN-HEAT-T for the calculated peak ZONE load
(see LS-A or LS-B for the ZONE peak load.)
Thanks for your help,
Kyle Nisonger
Mechanical Engineer, LEED(r) AP
US Army Corps of Engineers
Kansas City District
(816) 389-3224
-------------- next part --------------
A non-text attachment was scrubbed...
Name: LWood Dog Kennel B, Baseline - 2.inp
Type: application/octet-stream
Size: 92098 bytes
Desc: LWood Dog Kennel B, Baseline - 2.inp
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090914/f38f5c27/attachment.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: LWood Dog Kennel B, Baseline.pd2
Type: application/octet-stream
Size: 30914 bytes
Desc: LWood Dog Kennel B, Baseline.pd2
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090914/f38f5c27/attachment-0001.obj>
More information about the Equest-users
mailing list